Rewire
- Lake of the Ozarks
Is THHN suitable for wet location
Have you seen one thats not dual rated?Rewire said:Is THHN suitable for wet location
Dennis Alwon said:As mentioned above No, however most thhn wire is now both thhn and thwn wire. If it is just thhn then it is not suitable for wet if it is the combination wire then you are good to go.
Yeah, and if you're going to fill your pipes with oil and gasoline, make sure it says "oil and gasoline resistant". :grin:emahler said:if you are derating, use thwn-2......
mdshunk said:Yeah, and if you're going to fill your pipes with oil and gasoline, make sure it says "oil and gasoline resistant". :grin:
I couldn't resist.emahler said:take a look at 310.15 mr. smartypants...you can't use the 90D table for derating purposes if you use THWN in a wet location...
as for oil and gas...that's your problem![]()
mdshunk said:I couldn't resist.
By the way, if you want to wire a machine tool, make sure it says MTW on it too.![]()
emahler said:what type of wire would someone use to strangle a smartass from pennsyltucky?
Beats me, I would probably use...emahler said:what type of wire would someone use to strangle a smartass from pennsyltucky?
What's the ampacity on that, and what column do I use?chris kennedy said:Piano wire.
Greg Swartz said:What's the ampacity on that, and what column do I use?
Not covered.Greg Swartz said:What's the ampacity on that, and what column do I use?
90.2 Scope.
(B) Not Covered. This Code does not cover the following:
(6) Piano wire
Great, now you've done it,mdshunk said:Beats me, I would probably use...
some...ek, ak.... cough, cough... getting hard - to breathe.