Rewire said:
Is THHN suitable for wet location

As mentioned above No, however most thhn wire is now both thhn and thwn wire. If it is just thhn then it is not suitable for wet if it is the combination wire then you are good to go.
 

emahler

Senior Member
mdshunk said:
Yeah, and if you're going to fill your pipes with oil and gasoline, make sure it says "oil and gasoline resistant". :grin:

take a look at 310.15 mr. smartypants...you can't use the 90D table for derating purposes if you use THWN in a wet location...

as for oil and gas...that's your problem:D
 

mdshunk

Senior Member
Location
Right here.
emahler said:
take a look at 310.15 mr. smartypants...you can't use the 90D table for derating purposes if you use THWN in a wet location...

as for oil and gas...that's your problem:D
I couldn't resist.

By the way, if you want to wire a machine tool, make sure it says MTW on it too. ;)
 