Greetings, I came across something interesting here, hopefully one of you folks can explain....at a restaurant, 3- 200A 3 phase 120/240 42 space panels. Voltage readings were 120v to ground and neutral on A and C phase, B phase seems to have a high leg, of course, phase to phase readings were common 240V, I realized there were many single pole breakers on B phase !!!!!
I performed readings at breaker(s) output to ground and neutral and all were 120V !!, then I took readings again at line and load side of MCB , on B phase, ...180V ....bussing in panel was at 120V....:blink:....I am not understanding this !!!! , what am I missing here?, any input would be hopeful and helpful....THX....Dean