When the previous owners replaced the heat pump in 2005, the installers moved it to the other side of the pedestrian door located on the side of the garage. Probably because the line set, which is buried under the slab, was bad and it was easier to run a new one if the heat pump was moved. But for the electric, they switched from the existing GRC that came up out of the slab to PVC, ran the PVC up to where the old disconnect was and installed a "C" unilet there. They used the unilet to splice the existing #6 TW to #8 TW. Then they ran PVC up and over the door and down to the new disconnect.
The breaker at the panel was 50A and the disconnect they installed was a sub panel with a 50A breaker.
The fitting at the GRC-PVC was split and I wanted to get rid of the PVC going over the door. As I was tearing out the old, I noticed a #10 TW ground in the unilet. I knew there was only (2) #6 TW at the panel so I went to look for bonding to the GRC. There was none. At the disconnect I saw the same ground but nowhere did I see any other means of grounding. Once I started removing the wire I realized what was happening.
The installers inserted short pieces of #10 in the unilet and out from the conduit at the disconnect, where they landed it on the ground bus. :rant::rant::rant:
So for the last 12 years, this heat pump fed from a 50A breaker had no electrical ground and had to rely on whatever grounding it could get from the line set.
My wife asked if they just didn't know what they were doing. She's heard me complain about some of the shoddy workmanship I've found since we moved in a year ago. I had to explain to her this was purposeful and intended to fool the inspector. And obviously, it worked.
The breaker at the panel was 50A and the disconnect they installed was a sub panel with a 50A breaker.
The fitting at the GRC-PVC was split and I wanted to get rid of the PVC going over the door. As I was tearing out the old, I noticed a #10 TW ground in the unilet. I knew there was only (2) #6 TW at the panel so I went to look for bonding to the GRC. There was none. At the disconnect I saw the same ground but nowhere did I see any other means of grounding. Once I started removing the wire I realized what was happening.
The installers inserted short pieces of #10 in the unilet and out from the conduit at the disconnect, where they landed it on the ground bus. :rant::rant::rant:
So for the last 12 years, this heat pump fed from a 50A breaker had no electrical ground and had to rely on whatever grounding it could get from the line set.
My wife asked if they just didn't know what they were doing. She's heard me complain about some of the shoddy workmanship I've found since we moved in a year ago. I had to explain to her this was purposeful and intended to fool the inspector. And obviously, it worked.