caosesvida
Senior Member
I have 5 disconnects, from one service with 5 meters. Going to five trailers.
1. feed in with paralell 500 copper and 350 neut.
2. tap grounded condutors to each meter
3. meters to trough, 2" nipple
4. trough to disconnects, 2" offsets
5. disconnects bonded.
6. not using bonding locknuts
7. disconnects combo of 200-100-150 amp.
The grounded conductor is bonded to the meter at the meter, then bonded to the disconnect. The trough has a grounding lug with #6 going to the ground rod.
Is my trough properly grounded/bonded to the system, through the disconnects and the 2" offset. I feel like I should run a bonding jumper from the disconnect to the trough for some reason. Having the trough bonded through the offsets should allow any current a return path, but it seems like a #6 from the disconnects to the trough and to the grounding electrode seems more thorough. OR does this lead to more paths for a ground fault to follow? thanks for any thoughts on this.
1. feed in with paralell 500 copper and 350 neut.
2. tap grounded condutors to each meter
3. meters to trough, 2" nipple
4. trough to disconnects, 2" offsets
5. disconnects bonded.
6. not using bonding locknuts
7. disconnects combo of 200-100-150 amp.
The grounded conductor is bonded to the meter at the meter, then bonded to the disconnect. The trough has a grounding lug with #6 going to the ground rod.
Is my trough properly grounded/bonded to the system, through the disconnects and the 2" offset. I feel like I should run a bonding jumper from the disconnect to the trough for some reason. Having the trough bonded through the offsets should allow any current a return path, but it seems like a #6 from the disconnects to the trough and to the grounding electrode seems more thorough. OR does this lead to more paths for a ground fault to follow? thanks for any thoughts on this.