I did an inspection for the County today, and came across some engineers who would have preferred to see me buried beneath the concrete that was being poured on the job . Here is the situation/question.
There are two separate buildings that HAVE METALLIC CONNECTIONS between them.
There are 4 PVC raceways with 350 kcmil run in each PVC raceway, being supplied by a 1200 amp OCPD.
The engineers specified 3 AWG sized conductor for the equipment ground conductor. I told them the code required a size ?? AWG equipment ground conductor installed in EACH raceway.
What minimum size equipment ground conductor is required?
By the way - they told me that I had no clue about this and that the 3 AWG is sized fine. They also said a few other things , but this is not the proper place to repeat them.
Do you agree?