Worlds Gr8est Electrician
I went to a customers house to show her how to use her generator panel that she had had installed by a Lowes subcontractor.
She said she did not like how it looked and wanted me to make sure it was safe. Well I could tell right away this was gonna be a hack job when I saw the flex crammed in the top of the panel with no connector. The way he had this set up he was back feeding the fuse box with the generator with no way to prevent having the utility power and generator power on at the same time.
I told her what she had would not cut it and explained the problems with what she had. She just wants me to make it right. So she will be getting a new panel with a interlocking panel cover and a generator plug for her portable generator.
As you will see from the pics there are many things wrong with this panel. One being a while back she had a electrician come and replace her main disconnect and he did. The panel was fed with some old SEU so the ground was the neutral. When he changed the disconnect he ran a neutral over to the panel and isolated the grounds and neutrals. Well he pulled one Thhn for the neutral under the house and up through the bottom of the panel right through a ko no connector let alone the wire not being ran in pipe.
So I am going to re feed the new panel in pipe and THHN. Also at some point she had a dryer added well someone added a 2 space sub panel and fed it from the main lugs of the panel as you can see in the pics.
I went there to show here how to use her generator and ended up landing a pretty sweet job. I love panel change outs. On top of that she will have a much safer and neater set up.