Originally posted by Ed MacLaren:
I am interested in all opinions on this.
I think a good place to start is by looking at the two extremes.
One; lets assume the panel is completely isolated, like it is magically floating in air, absolutely no return paths availible. If that were the case, then full voltage would be applied to the enclosure, no OCPD would operate. The victim would be the only return path and considered a normal load.
Second is to assume the ground or fault impedance to be zero. The OCPD would operate. The case would remain at zero potential even during a fault. The victim would be in parallel with 0 ohm?s, and would not receive a shock.
The reality is neither is likely to be true, and the answer lies somewhere between the two extremes. Even if they?re no GE connections, there is likely to be some unplanned return path like a raceway, building steel, concrete, etc. This would form a simple voltage divider circuit. The enclosure would go up to some potential for the victim to be exposed too. How much, who knows, too many variables but IMHO, it is closer to the first scenario.
Edit:
Now for something realistic. Lets say the EGC is in place, the EGC is the same size as the ungrounded conductors, and there is no supplemental GE connection. During a fault, a simple voltage divider is formed by the ungrounded conductor and EGC. Since both of these conductors take the same route, same size, and same length, it is reasonable to assume the voltage on the enclosure would be approximately 1/2 the supply voltage. That voltage would remain on the enclosure for the time it takes the OCPD to operate. The victim would receive a shock until the OCPD operates.
[ January 10, 2005, 05:15 PM: Message edited by: dereckbc ]