Replying to the first, IT DOES BOTHER ME BIG TIME AS WELL. I guess we think alike.:roll: Now, Utility aside, in my opinion bonding to the water main has its benefits. The metallic water pipes make the best ground rods, especially when part of a municipal system. As a result it forms a redundant mesh, which is best for equal potential and contingencies such as an open service ground (normally the neutral). Also is the added protection that when a live phase comes in contact with a water line there is a near complete guarantee that enough current will flow to clear the fault. And lightning protection to could be argued as enhanced.
However, these are not the only reasons and not the only influence behind the water bonds. And Utility practices make it look awful. In the real world water lines are the utilities biggest neutral, aside from the earth itself and the common neutral on the poles. And of course the phone shield wires as well and Im sure others are being left out. The NEC does try to limit stray current as much a possible (heck one can not use a ground bar as a neutral bar at the service entrance because the current can flow over the enclosure to the bond screw), but keep in mind the NEC is influenced by outside sources as well like the Utility industries. A service is the point where the NESC (usually the code utilities choose to follow) ends and where the NEC begins. The NESC and NEC do contradict themselves frequently, and at the service is where the two fight to blend together with out issue. The NEC has to give in, in this area to get things to work out.
And I think our obsession with water bonds was pushed the most by utilities. By adding a water bond at each service the utilities get a free super neutral and free lightning protection at the customer's expense. Utilites treat ground, earth and neutral as the same thing to save costs. The water bonds save a utility a larger neutral, ground rods, grounding grids, lightning arresters, headaches from broken neutrals, ect and as a result using single bushing transformers/primary wye grounded becomes easy with less worry for them. The primary wye further gives savings for reasons to much for me to go into now.
Now the end result that I am not found of: Current is always dividing between the neutrals and ground/other metal objects. The outcome from this is EMFs, stray voltage/elevated touch potentials and shock/electrocution. Summarizing the 3:
>EMF because of the inability for all current to cancel in a race way/cable/conduit/wire bundle ect because often half if not more of it is going somewhere else. EMF though debatable, could be a health risk. And when one considers the the fact North America has higher cancer rates over other countries where such practices are rare ... well lets just say conspiracy theorists and those in the field of non-ionizing radiation have something to think about. And If it is to be proven a health risk that info might never come out for obvious reasons the utilities could get sued by many.
>Stray voltage and touch potentials. Comes from voltage gradients caused by varying resistance across objects with voltage being pushed through them. Think voltage drop across a wire. The problem is real and has been seen before both effecting people and animals: Reports of people being killed and shocked in lakes from corroded neutrals is one. Another and the biggest are complaints from dairy/animal farmers who have encountered the problem all over the the country loosing livestock production.
>This one hits home for some plumbers and electricians: A water bond masks either a failed low voltage neutral or a failed high voltage neutral or both. Examples: A neighbors failed neutral will cause his current to go from his water bond through the water pipes in the street up through your water bond and go back via your intact utility neutral. Another scenario is a high voltage neutral that has completely deteriorated in an underground cable network or failed from say a broken tree limb hitting a pole, all current from the transformer primary then travels through the HV-LV neutral jumper, through your service, water bond and then back to the substation. Both these can go unoticed for years and usually do until work is done on water pipes, water meters, grounding system ect the danger makes itself known, sometimes even killing. Nothing like doing a service change (because the panel was an FPE:roll
with the water bond arcing up a storm and then seeing the fire department arrive next door because the neighbors electronics started smoking:happyno:
And on a quick side note, when utilies use the neutral to double as a ground, low level ground fault protection goes out the window. Substation feeder breakers and reclosers no longer can be set to trip out at say 5 amps but instead set to trip at hundreds. Good luck detecting downed lines during storm:lol:
Now onto question number 2.
In my opinion water heaters should be required by code to have GFCI protection for the very reason you state along with dishwashers, clothes washer, ect. Unfortunetly attention has drifted to psedo-science that warants the use of AFCIs
I guess it might not be a risk because the water heater is grounded as are the water pipes. But again GFCIs make a world of difference.
Sorry about the long post but I was in thinking mode. Hope my info was on the money.