Came across this on a farm. What're your thoughts other than compression connections are suggested. More often than not Im seeing contractors use whatever they can to connect to the transformer. Usually, these systems are maxed out and pumping power back to the grid through this connection for 9-12 hours a day.
 

Attachments

  • orig_image_1 - 2020-12-20T094708.360.jpg
    orig_image_1 - 2020-12-20T094708.360.jpg
    143.9 KB · Views: 58
One issue I'm seeing, is that the surface of the lugs is not entirely in contact with the transformer stabs. There is about a 1" overhang beyond the transformer stab. The listing of the lugs is likely based on the lug being in contact completely with the busbar.
 
I prefer the wire connections to be as close to where the bushing leaves the transformer. I don't like to see the leverage placed on the bushing by putting the conductors out at the end.

I also don't like the lugs hanging over the bus.
 
I prefer the wire connections to be as close to where the bushing leaves the transformer. I don't like to see the leverage placed on the bushing by putting the conductors out at the end.

That's a good point too. Bear in mind that it is common to build the secondary stabs with insulated support hangers from the ceiling of the cabinet. This image shows black rods with female threads holding the threaded support rods, that serve this purpose. This relieves the bushing of all that leverage from the weight of the cables.
 
That's a good point too. Bear in mind that it is common to build the secondary stabs with insulated support hangers from the ceiling of the cabinet. This image shows black rods with female threads holding the threaded support rods, that serve this purpose. This relieves the bushing of all that leverage from the weight of the cables.
I did not catch that, and have never seen that in the field. Thanks.
 