Truly is that simple , the checks are a good analogy. load calcs. 101If I ordered two boxes of bank checks instead of just one, would that mean I can spend more money?
The ratings of the panels and the rating of the service are not relevant to your question. What matters is the calculated load. If it is lower than 200 amps, then you can feed as many panels as you wish.
Only other comment I have is your meters are cold sequenced (after the service disconnect) which is odd to do with under 7 meters. Check with your POCO if u haven't.In a commercial application can I feed three 100 amp meter/main panels from a 200 amp service? The 200 amp disconnect will be rated 22,000 AIC. and feed into a gutter to feed the three meters. Or do I need to have a 320 amp main?
NEC doesn't even require the disconnect on the supply side in that situation and when there is more than one service disconnecting means the supply conductors only have to be sized to the load calculation and not the total overcurrent devices.Only other comment I have is your meters are cold sequenced (after the service disconnect) which is odd to do with under 7 meters. Check with your POCO if u haven't.
I have two comments, one about this quote and one more general. The more general one: Make sure you meter/mains are not "suitable for use ONLY as service equipment. That means you cannot separate the neuters and grounds which would be required (there is 250.142(B) exception #2, but I dont think that can be applied as you have a meter/panelboard combo not just a meter socket, and further, not sure if they can all be "immediately adjacent to the service disconnect).I want to put in one 200 amp fused disconnect to meet the 18,000 AIC requirement. Do the 100 amp breakers need to meet the 18,000 interrupt rating too?
What do you have. Is pretty common to see main breaker with 22k rating or even 25k and branch breakers that are 10k but series rated for use with the main.I want to put in one 200 amp fused disconnect to meet the 18,000 AIC requirement. Do the 100 amp breakers need to meet the 18,000 interrupt rating too?
Couple things - unless all three are in close proximity there is often good chance conductor impedance by the time you get to final device reduces the available current at that point to a level where you won't need to look at series ratings.Yes but he has three breakers in series so one has to be careful in these situations. A very common mis-application of series ratings is with 3 OCPD's in series, A-B-C, to series rate A-B, and then series rate C with the series rating of B. That is not allowed. IT is allowed to insert a fully rated OCPD in between or ahead of a series rated pair and that should be no problem for the OP: He fully rates the 200, fully rates the 100's, and series rates the branches to the 100's. Another option is to rate A-B and A-C as long as A-C has the same (or higher) interrupting level as A-B.
some cases you might have a MDP device that is series rated with the final device - if so does it really matter what is in between? Again distance may reduce current at the end anyway. If all in same vicinity, somewhat unnecessary to have say MDP feeder breaker - main breaker in panel - branch circuit breaker when you already have a panel disconnect within sight of the panel. Of course that panel main still needs rated for available current at it's location or be series rated with the one ahead of it.
Yes, I played around a little with fault calculator spreadsheet, starting at 65k is difficult to get level down to below 22k without at least 100 foot run and still needed even more length for 200 amp conductors.Certainly taking into account conductor impedance can help avoiding having to use higher or series rated equipment. The AFC in the OP is pretty low. But take a service that has 65K at the service disconnect, its going to take quite a bit of length to get down to 10k.
The main thing you cant do, which many do, is the following: Three devices A-B-C, main distribution and branch respectively. Say AIC of A is 65k, B is 22k, C is 10k. AFC at line side of A is 65k, AFC at line side of B is 50k, AFC at line side of C is 20k. A and B series rate. B and C series rate. Many find it acceptable to use these three in a series but it is not acceptable unless A and C rate at the same level as A and B.
starting at 42k seemed to be able to come up with some scenarios where I could get a 100 or 200 amp feeder that isn't real long and have under 22k at the load end.
I can't recall ever needing to do real world calculation that involved 65K available, have done some that get into ~40k range a time or two.You can actually typically get a series rating from 65k all the way down to 10k miniatures, but the distribution has to be 225 or smaller frame size. I think square D has a couple that will go 400 frame @ 65k all the way down to 10k but nothing higher than 400.