I apologize for insisting on 180 va/bathroom receptacle. i am just trying to correctly grasp the procedure to calculate the correct load for a real residential project.
The meter is 240 v single phase 3 wire 400 A/320 A continuous meter.
There are 2 mains, each with a 200 A breaker. The 1st main feeds an 8 circuit bus in the G.E. enclosure itself. It also has pass-thru lugs at the bottom of the bus which I may use in the future to feed a pool panel.
I want to feed the 2nd floor panel with a 100 A breaker from the 8 circuit "mini-panel" ( over 25 ft away..10 / 25 ft tap rule ) and keep the rest of load available for future swimming pool and car charger. The 2nd floor is approximately
1400 sq ft and has 3 bathrooms, each "counter" receptacle separately fed by it's own 20 A breaker. It also has the 2nd floor AHU, part of a heat pump system without a back-up heater. ( job is in south Florida, owner does not believe a back-up heater is necessary..) There is minimal load on the upstairs panel, so the future looks bright for the future pool equipment and possibly a car charger. I would ( if this is correct ) figure this at 1400 sq ft at 3 watts / ft.
There would be no range or water heater on this panel, but the 2nd floor does have a washer and a dryer. Could I also use Sokolnik's
spread sheet to figure the wire size to feed the 125 A main lug panel ? (using a 30 space 30 ckt full size brkr panel )
Do I do a standard or optional load calc on the 100 amp breaker for calculating the feed to the 2nd floor panel ?
And do I do a standard or optional calc for the 200 amp breaker feeding the 8 ckt panel including the loads of the
100 Amp brkr feeding the 2nd floor panel ?
The first floor includes the kitchen and is approx 1650 sq ft. I would feed this at 200 Amps ( may be less..depending on calcs...) the breaker for the 1st floor has not been purchased yet. The property is presently unoccupied and is being fed by a temporary service while the electrical plans are being revised. It will feed the 2 heat pump condensers, the 1st floor ahu and asstd kitchen and other appliances. Do I calculate this at 1650 sq ft @ 3 watts a sq ft. ? Can I use Sokolik's spreadsheet to calculate the feeder size ? Do I need to use standard or can I use optional calculation ?
Can I use the calculated load for feeder sizing ?
Finally, when this is done, do I do a TOTAL calculation for the entire service, including all items at 3050 sq ft ?
Sorry about the dumb questions, but I was told this was the way to do the calcs by an electrical engineer I have known for over 15 years... I am 70 yrs old and still learning.....
Thanx, dhsvcs