Three ph 480V convenience (welding) recepts

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Is there anything in NEC that talks to max number of 480V receptacles you can load on single branch circuit? I’ve seen up to 4, 60A welders on a 100A circuit.


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I'd like to think it was not permissible due to the fact that it is a welder allowance and nothing assures other type equipment might not be plugged in. Perhaps another member can correct my interpretation,
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
I'd like to think it was not permissible due to the fact that it is a welder allowance and nothing assures other type equipment might not be plugged in. Perhaps another member can correct my interpretation,

If the recepts are internally fused. I believe you can put more than 2 on a circuit


Sent from my iPhone using Tapatalk
 