FewerSparks
Member
I have a task where I have a Motor Control Center with several motors. Per NEC, I have used 1.25% of the largest motor and 100% of the remaining motor (Full Load Amps) and have come up with a load of 473 Amps. For sizing my main circuit breaker, would I use a 500 Amp breaker or do you have to apply the 125% rule to the 473 Amps (1.25 x 473 = 591 Amps) and go to a 600 Amp breaker.
For the conductors, are there any other code requirements for the size (like another 1.25) or do I just select the conductor with the ampacity for the circuit breaker you use?
For the conductors, are there any other code requirements for the size (like another 1.25) or do I just select the conductor with the ampacity for the circuit breaker you use?