Three phase 480 V 4 wire wye service ampere check

Status
Not open for further replies.
The amp readings were re-shot, interestingly found one of the six conductors on each phase read high. Ended up using method suggested to calculate total amp load on the service gear. ( thanks guys) It was 602 amps.

The reason for doing this is to determine the actual load on a new 680 KW emergency mobile generator that arrived today that we subsequently hooked up with type G-GC 2000V MSHA trailing cable. This hook up required three parallel cables to carry the load.
 