Three phase 480v 400 amp surge protection

JJWalecka

Senior Member
Location
New England
Couple questions.

Will a 480 volt 400 amp panel with surge protection protect the secondary side of a transformer feeding a 120 volt panel?

There is a three phase 400 amp main panel what surge protection is listed and or would you recommend
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Couple questions.

Will a 480 volt 400 amp panel with surge protection protect the secondary side of a transformer feeding a 120 volt panel?

To at least some extent. The transformer itself will also provide some protection to downstream devices from upstream surges.

There is a three phase 400 amp main panel what surge protection is listed and or would you recommend
If there is room in the panel get whatever the panel maker supplies that just snaps in, otherwise, it does not matter much. Get whatever your supply house has available.
 