I sent this question directly to Mike although I believe this is the correct process, I apologize for my error!
A student posed a question that I cannot answer other to say, "That's the way it is."
Appendix "D", Sample D3 (a). The method used to calculate the Ampacity of the 3p load. Subtotal, actual load (actual load in amperes) formula
99,000 VA / (480V * 1,732) = Ampacity
99,000/ 831 = 119 Amps
The question is, why are we multiplying a 3p voltage, 480V by 1.732 because 480V is already a 3p voltage.
Can anyone answer this question, please.
A student posed a question that I cannot answer other to say, "That's the way it is."
Appendix "D", Sample D3 (a). The method used to calculate the Ampacity of the 3p load. Subtotal, actual load (actual load in amperes) formula
99,000 VA / (480V * 1,732) = Ampacity
99,000/ 831 = 119 Amps
The question is, why are we multiplying a 3p voltage, 480V by 1.732 because 480V is already a 3p voltage.
Can anyone answer this question, please.