Never seen this before and need to know if it is a violation.
Single phase furnace connected to a three phase breaker. If allowed would it mater which phases the equipment is connected too?
No violation. No problem unless its a 240 delta high-leg system in which case one would need to be careful as to phase.
It is line to line with no neutral, the rest of what you are saying I do not understand.
Straight rated means it is rated for 240V between any two phases, or any phase and ground. It is rated for any way you can connect 240V in the system, or whatever its rating may be.
Slash rated means it is rated for example, 120/240V, and both those numbers are important ratings. It is rated 240V between any two phases, but the voltage between any phase and ground cannot exceed 120V. Good for most applications, but problematic if it connects to the high leg in a 120/240V delta system, where the high leg b-phase is 208V phase to ground.
Mostly the fact that the slash rated breaker has a maximum line to ground voltage (nominal) of 120V and connecting one of its poles to the high leg exposes it to 208V to ground.What would be problematic about it?
JAP>
It is not a voltage issue, it is a fault clearing issue.Mostly the fact that the slash rated breaker has a maximum line to ground voltage (nominal) of 120V and connecting one of its poles to the high leg exposes it to 208V to ground.![]()
It is not a voltage issue, it is a fault clearing issue.
Mostly the fact that the slash rated breaker has a maximum line to ground voltage (nominal) of 120V and connecting one of its poles to the high leg exposes it to 208V to ground.![]()
The the energy that the breaker has to interrupt is higher when the ground fault is 208 volts to ground as compared to 120 to ground.??? Please explain.:?
Thank you. I was not aware that was the main design difference in a slash rated breaker.The the energy that the breaker has to interrupt is higher when the ground fault is 208 volts to ground as compared to 120 to ground.
Does that mean that a 120/240 slash rated breaker could be used at 208V to ground with a reduced AIC rating? I mean physics-wise, not listing-wise.The the energy that the breaker has to interrupt is higher when the ground fault is 208 volts to ground as compared to 120 to ground.
Still don't make sense.
When would one ever use the wild leg and a neutral to feed anything other than a subpanel?
JAP>
Maybe, but you would have to get the AHJ to sign off on the code violation.Does that mean that a 120/240 slash rated breaker could be used at 208V to ground with a reduced AIC rating? I mean physics-wise, not listing-wise.
Cheers, Wayne
I kind of wondered the same thing. Seems like the main thing is how much energy may flow during a fault, and you could easily have a open delta system that has pretty limited capacity on the high leg transformer, yet have a 167 kVA single phase transformer that has much higher fault current though it is only 120 volts to ground.Does that mean that a 120/240 slash rated breaker could be used at 208V to ground with a reduced AIC rating? I mean physics-wise, not listing-wise.
Cheers, Wayne