gjs2.power4
New member
Are the actual ammeter reading per phase in a three phase system is the three phase current? or it will be multiplied by square root of three to get the three phase current in computing size of interrupting device.
Then you are making a calculation. The OP was about a measurement.What about when you are calculating the size of the overcurrent device for a three phase delta resistance heater?
My view is that the notion of "per phase current" is meaninless.
Please allow me to suggest that what you are interested is the current "in each phase." The word "per" carries with it the connotation of multiplication, and that is the part that is meaningless. For example, you get the total price of 3 dozen lemons at $4.00 PER dozen by multiplying 3 times $4.00.. . . At this point I really do not care about the KW, KVA or even the 'total current' only the current per phase.
As others have said, it is the current in each phase that is used for sizing the interrupting device. Normally, however, you would not use measured current, but would calculate the maximum current.Are the actual ammeter reading per phase in a three phase system is the three phase current? or it will be multiplied by square root of three to get the three phase current in computing size of interrupting device.
Thanks Charlie. This is how I have been doing it but I caught this thread and thought I would double check my work.The heater is not going to be able to tell the difference between its source being delta connected or being WYE connected. The OCPD is downstream of the source, and it just has three wires to deal with. The current in any wire is going to be the same as the other two, presuming again that the load is balanced. So you take the total three phase watts of the heater, divide by the voltage of 208V (presumably you are talking about a 120/208 volt system), and divide again by the square root of three. Then you multiply by 125% because this is a continuous load. Finally, you select the next higher standard size OCPD (unless you are over 800 amps, but I doubt that that is what you are asking about).