I looked at a residential job that has a separate service for a pole barn that supplies 120/240v 3phase with a 208v high leg. My voltages read fine with no load.My problem is that any 120v. load you put on the A or C phase (B phase is the 208v) I get different voltages. ie. A phase drops to 60 volts and C phase increases to about 180v. The 500 watt halogen light that I was using to test was always dim.
I tried to reconnect the neutral at the service mast where it connects overhead from the poco. This didn't chang anything. Please advise.
Ed