We were called to a job to check a motor generator issue, the motor generator was off line and the customer?s art ($21, 000, 00.00 worth) was getting warm, and humidity was exceeding determined levels.
What we found was the following. The contractor had installed the specified 3 phase chiller, and the utility was going to install 3 phase service, but coordination was off. The utility originally quoted about 1, 000,000.00 for 3 phase service, after review the revised cost was a bit over $5,000,000.00. So a second option was proposed, install 3 parallel 3 phase rotary converters. But it seems the chiller phase monitor would not operate with the 3 phase voltage A-B 208, B-C 208, C-A 240. The chiller manufactured said this would void the warranty. So the contractor installed a 100 HP motor generator (motor generator manufacture modified the MG operational controls to permit input voltages at this level) fed from the phase converters that then fed the chiller.
Final outcome the system cost a lot to install and is about 36% efficient at full load. And lastly the Diesel generator (not the motor generator) that was installed to back all this up blew up 3 days after warranty expired.