- Location
- Orange Park, FL
- Occupation
- Automation Systems Engineer
Working on a motor which will be on a floating deck in the middle of an 80 foot diameter dunnage pond. Supply voltage is 480 via VFD and looking at the VFD literature it has ground fault detection built in when there is a difference in current detected at 25% of the drives rated amperage. For this application that would be a 13 amp difference. Which made me think... I should look to see if any other ground fault protection needs to be provided based on 2020 NEC. Both 682.15, and 210.8(B) only carry requirements for single phase and I had to stop and ask why? I know there are GFCI for 208V VFD systems, and while I realize a Class A GFCI has a maximum voltage limitation of 240V I still can't understand why there would not be a requirement for a 480V system running a motor in the middle of a pond to have ground fault protection per code. Can someone help me understand why there seeems to be no requirement for 3 phase circuits?