I am struggling recreating an issue that was reported on a site where there are several breaker synchronization devices (has three phase PT and CT inputs) that is reading voltage at the breaker and current across the breaker but is reading 0 kW for real power and 183 kVar for reactive power. Each phase voltage is 450 V and each phase current is 590 A. I am not able to determine the phase angles with this device.
The CTs are 1500:5 A and the PTs are 400:100 V. The PT wiring is a 3PH3W for a delta system.
With the real power reading 0 kW with each phase having current, it appears as though the wiring from the CTs could have been swapped between any two phases. In a balanced system, which this is, this would be the case. However, the same would also be true for reactive power. If the issue was in fact swapped CT phases, then we would read 0 kW and 0 kVAR. This is where I am struggling to theorize the reason for this reading. Assuming there is something wrong with the wiring, what possible error could cause the meter to read a fully reactive load with no real load?
The CTs are 1500:5 A and the PTs are 400:100 V. The PT wiring is a 3PH3W for a delta system.
With the real power reading 0 kW with each phase having current, it appears as though the wiring from the CTs could have been swapped between any two phases. In a balanced system, which this is, this would be the case. However, the same would also be true for reactive power. If the issue was in fact swapped CT phases, then we would read 0 kW and 0 kVAR. This is where I am struggling to theorize the reason for this reading. Assuming there is something wrong with the wiring, what possible error could cause the meter to read a fully reactive load with no real load?