ddkeith

Member
can someone help me out on this? i need to know how how to size a three phase service panel in amps. is it done the same way as a single phase where you take the net caculated load va and multiply by supply voltage? and does it make a difference if theres a high leg or not? thanks in advance.

keith
.
 
Re: three phase service panel

Originally posted by ddkeith: . . . is it done the same way as a single phase where you take the net caculated load va and multiply by supply voltage?
I believe you meant divide by. It does work essentially the same way. But as Bryan pointed out you also divide by the square root of three (about 1.732).
 