I am trying to work backwards and see if I can get similar answer based on the information provided from the Electrician.
The system is 208V/3Ph system.
We have a value of 41,748a at the secondary taps of the utility transformers provided by the utility company.
Length of run from transformers to tap box is 185’. The conduit is (3) sets of 750 aluminum PVC conduit. The fault at the Tap Box is 22,874A
Length from Tap box to meters is 20’ of copper bussing. The conduit is (3) sets of 750 aluminum PVC conduit. The fault at the meter is 21,986A
Length to unit A is 100’ (1) set of 3/0 copper steel pipe. The fault at Meter A is 10,962A.
I am trying to use the Eaton app and do the hand calculation by hand. But I don't think I am getting the right KVA or Z% for the system.
I am assuming the electrician used a infinite bus for his calculation.
The system is 208V/3Ph system.
We have a value of 41,748a at the secondary taps of the utility transformers provided by the utility company.
Length of run from transformers to tap box is 185’. The conduit is (3) sets of 750 aluminum PVC conduit. The fault at the Tap Box is 22,874A
Length from Tap box to meters is 20’ of copper bussing. The conduit is (3) sets of 750 aluminum PVC conduit. The fault at the meter is 21,986A
Length to unit A is 100’ (1) set of 3/0 copper steel pipe. The fault at Meter A is 10,962A.
I am trying to use the Eaton app and do the hand calculation by hand. But I don't think I am getting the right KVA or Z% for the system.
I am assuming the electrician used a infinite bus for his calculation.