You are not. I agree with you.Originally posted by iwire: Why would I not simply choose conductors rated 200 amps or more and forget about the calculations? . . . Am I missing something?
That would drive me nuts. :roll:Originally posted by charlie b:
However, I recently reviewed a design in which all of the sub-panels (large building, there were a bunch of panels) were 225 amp, regardless of the load. There might be a 50 amp OCPD and 50 amp feeder conductors, but the panel was shown as 225 amps.
The neutral would only be a current carrying conductor if a major portion of the load was non-linear. At that point derating would apply. Otherwise the 3/0 that iwire suggested would be fine.i also thought that 3/0 would be sufficient but..
is the neutral considered current carrying? looking @ 310.15(b)(4) i would say no.
this is being installed in conduit, so would derating be necessary and make the 4/0 proper?