A 150KVA 480/240v three-phase delta-delta transformer is protected primary side by a 225-amp circuit breaker. The secondary is corner grounded and the secondary conductors are comprised of 2-4/0 AWG THWN-2 Cu conductors per phase and a No. 2 AWG bonding jumper in each of two 2-1/2 inch conduits. The secondary conductors run 150 ft. to an auxiliary gutter where they are tapped to supply five 60-amp fused switches and two 100-amp fused switches. The calculated load is 360-amps. 
 
1) Does this installation comply with the code?
 
2) What is the required bonding jumper size between the auxiliary gutter and the 100-amp switches and the 60-amp switches assuming the tap conductors are No. 1 Cu. and No. 4 Cu respectively?
	
		
			
		
		
	
				