When going from a 3 phase delta delta 3,800 volt primary to 480 volt secondary for a 300 KVA transformer
which then feeds another step down transformer for a black smith shop
The blacksmith shop’s transformer is 25 KVA 480 volt primary to 240/120 secondary
Then, if feeding from the 3 phase 300 kva delta transformer secondary to a 25 kva single phase transformer in the blacksmith shop, do you treat the equation as a single phase system or 3 phase system including the square root of three to find input and output amperes at single phase transformer? (Just asking because source is 3 phase)
KVA/ secondary voltage
Or
KVA / secondary voltage x 1.732
I believe we don’t use 1.732 even if coming in with a three phase transformer to feed a single phase transforner
Also does it matter if using a, b or b, c or a, c phases from 3 phase system to feed single phase panel?
which then feeds another step down transformer for a black smith shop
The blacksmith shop’s transformer is 25 KVA 480 volt primary to 240/120 secondary
Then, if feeding from the 3 phase 300 kva delta transformer secondary to a 25 kva single phase transformer in the blacksmith shop, do you treat the equation as a single phase system or 3 phase system including the square root of three to find input and output amperes at single phase transformer? (Just asking because source is 3 phase)
KVA/ secondary voltage
Or
KVA / secondary voltage x 1.732
I believe we don’t use 1.732 even if coming in with a three phase transformer to feed a single phase transforner
Also does it matter if using a, b or b, c or a, c phases from 3 phase system to feed single phase panel?