Three phase voltage drop

Status
Not open for further replies.

ecvolt

Member
I have used this calculation for three phase E drop is it ok ? 2xKxDxI divided by allowable e drop=CM of wirex.866 note for three phase is this ok thanks ED
 
My Herman book describes this formula use for odd timing of current peaks in 3-phase systems, by multiplying wire length by 0.866. However, without engineering supervision NEC compliance restricts me to the properties listed in NEC Tbl.310-16(-86), & Tbl. 8 & 9, based on 1000 foot lengths.

Iduno if that 3-phase 0.866 factor was built into the 1000.ft figures on table 9, which deals with 3-phase XL, R, & Z values, but I'm not allowed to modify the conductor properties or lengths listed there. Maybe engineering supervision that uses NEC Appendix C formulas to develop specs. for prints, can also use other formulas?

One effort to develop a Target Voltage template based on these NEC tables was last discussed with this Unusual Power Distribution Setup.
 