three prong outlets

Status
Not open for further replies.
Location
lynnwood washington
Occupation
electrician
If you have old ungrounded wiring and two prong outlets, and you protect the circuit with a gfci breaker , is it permissible to install three prong outlets? I've been told different things about this subject
 
See 406.4(D) for non-grounding receptacle replacements, my interpretation is that applies except for equipment listed in 250.114(3). See also 250.130(C)
 
Yes you can, but you need to add the ”GFCI protected circuit” AND the “no equipment ground” label.
Even if it doesn't serve a purpose, why would that be an issue?

JAP>

My understanding is that if someone opens up the receptacle box and sees the EGC connected, it would be a natural assumption that the circuit is grounded, when in fact it’s not.
 
In that case hasn't the GFI protection you've just installed failed you?
The idea is to not risk creating a greater hazard from new wiring.

The GFCI device will only trip after a person has received a shock.

It will not trip just because a second load has become energized.
 
I looked up the rule and is does guide you to not terminate the EGC in this instance.

That's smart.

I wasn't aware of it.

JAP>
 