CanadianDave
Member
- Location
- Edmonton, Alberta, Canada
- Occupation
- Electrician Inspector
I have a situation that is a first for me, and I'm looking for some confirmation and confidence boosting.
I have a three-phase supply fed from a grounded neutral wye secondary, but the neutral conductor is not brought out from the transformer. This secondary feeds into a motor control center that currently feeds only three-phase motor loads (that drive various pumps in a water treatment plant). Engineering has designed a circuit to feed three exterior buildings, one Power Distribution Center (PDC, or e-house) and two battery storage buildings (all three buildings associated with a new solar array). This circuit will provide base building power for these three buildings, but will not connect to the array. Each building is designed to be supplied by two phases of the three phase supply, connected line-to-line and will supply single phase primary, split phase secondary transformers to create 120/204 for lighting, receptacles, HVAC, fire alarm, battery monitoring equipment (but not battery charging), and other, general building loads. The PDC load is approximately two times the load of one of the battery buildings. My questions are as follows:
1. Are the line-to-line voltages going to be affected by the unbalanced loads and floating neutral, given that there are no line-to-neutral loads in the feeder circuitry? If so, to what extent?
2. The MCC will be bonded to the metering cabinet in the PDC (first point of termination for the supply circuit) with the bonding conductor in the feeder cable (the neutral conductor is to be capped and spared). Under fault conditions, will the bonding connection be sufficient to activate the overcurrent device in the MCC, given that there is no neutral in this portion of the circuit?
3. Would a line-to ground fault cause a situation where equipment enclosures could become energized, while the system continues to operate, such as in an ungrounded delta circuit?
My gut is telling me that the neutral needs to be continuous from the first transformer star point, through the MCC and into the metering cabinet, but the design engineers are telling me that I'm worried about nothing. Any suggestions?
I have a three-phase supply fed from a grounded neutral wye secondary, but the neutral conductor is not brought out from the transformer. This secondary feeds into a motor control center that currently feeds only three-phase motor loads (that drive various pumps in a water treatment plant). Engineering has designed a circuit to feed three exterior buildings, one Power Distribution Center (PDC, or e-house) and two battery storage buildings (all three buildings associated with a new solar array). This circuit will provide base building power for these three buildings, but will not connect to the array. Each building is designed to be supplied by two phases of the three phase supply, connected line-to-line and will supply single phase primary, split phase secondary transformers to create 120/204 for lighting, receptacles, HVAC, fire alarm, battery monitoring equipment (but not battery charging), and other, general building loads. The PDC load is approximately two times the load of one of the battery buildings. My questions are as follows:
1. Are the line-to-line voltages going to be affected by the unbalanced loads and floating neutral, given that there are no line-to-neutral loads in the feeder circuitry? If so, to what extent?
2. The MCC will be bonded to the metering cabinet in the PDC (first point of termination for the supply circuit) with the bonding conductor in the feeder cable (the neutral conductor is to be capped and spared). Under fault conditions, will the bonding connection be sufficient to activate the overcurrent device in the MCC, given that there is no neutral in this portion of the circuit?
3. Would a line-to ground fault cause a situation where equipment enclosures could become energized, while the system continues to operate, such as in an ungrounded delta circuit?
My gut is telling me that the neutral needs to be continuous from the first transformer star point, through the MCC and into the metering cabinet, but the design engineers are telling me that I'm worried about nothing. Any suggestions?