gcassi said:Is it acceptable to run a three wire (No Grounding wire) to a detached garage as long as I install a rod at the detached garage panel.
Not in all cases pipemaster. If you have a metal water pipe or metallic raceway between the 2 structures then you must run an equipment grounding conductor.pipemaster said:Sure you can. This panel would basicly be handled as a new service. The neutral will have to be bonded again.
Thanks Roger. I couldn't find my code book.roger said:Pipemaster, as Pismo points out, if there is any electrically conductive paths between these buildings the three wire option is out. Read 250.32(B)(2) for the specifics.
Roger