Hello All,
I have a question on short circuit test for panelboards. I read online that the panelboards have a 3 cycle withstand rating (0.05s) based on UL standard. My question is most of the breakers which are installed as the Main typically may take more time (worst case) than 0.05seconds to open and clear the fault.
As per my interpretation the short circuit test is based on the through fault (branch breakers) rather than the main. So the 3 cycle rating is for the through fault not for internal fault. Is my thinking correct on it. And what is considered to be protecting for the internal bus faults?
I have a question on short circuit test for panelboards. I read online that the panelboards have a 3 cycle withstand rating (0.05s) based on UL standard. My question is most of the breakers which are installed as the Main typically may take more time (worst case) than 0.05seconds to open and clear the fault.
As per my interpretation the short circuit test is based on the through fault (branch breakers) rather than the main. So the 3 cycle rating is for the through fault not for internal fault. Is my thinking correct on it. And what is considered to be protecting for the internal bus faults?