THW in Operating rooms????

Status
Not open for further replies.

maddawg-

Member
I have heard that there is a standard about requiring type THW insulation for circuits in operating rooms. Can anyone elaborate on that, and tell me where that is found, and why?

Thanks for the info,
Scott
 
Re: THW in Operating rooms????

Scott, if you are talking about O.R.'s served with isolation power systems, this would be XHHW for it's dielectric constant. Manufacturers require this in their information with the isolation system equipment.

The NEC doesn't directly state XHHW, but does recommend a dielectric constant of 3.5.

Read 517.160, specifically 517.160(6) and the FPN's.

Roger
 