You got the name wrong (I've fixed it). They look nice but might have code issues with securing.

 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Yes, unlike some of the raceway articles that only require securement within 3' of the box, and just support between the securement points, the rule in 334.30 requires support and securement every 4.5'. These would require the use of something like a cable tie for the securement, but would still likely reduce the costs as compared to individual staples.
 