Following is a link to the NFPA for a TIA that is being proposed to remove the requirement for perimeter surface bonding (680.26(B)(2)) at listed, self-contained, outdoor spas and hot tubs as currently required in 680.42 of the NEC.
The premise of the proposal is that self-contained spas and hot tubs should be exempt for the perimeter bonding requirements much like storable pools and indoor spas as permitted in 680.30 and 680.43 - Exception 2, respectfully, of the 2011 NEC.
This has certainly been a hotly debated issue since the inception of the permiter surface bonding concept back in the 2005 NEC. While many code professionals and users have come to grips with all the requirements of 680.26, it has always been a gray area as to how the perimeter surface bonding is to be accomplished for a self-contained spa installed on an existing slab.
While the acceptance of this TIA would only change the 2011 NEC, it may be used as substaniation to not require the bonding of the perimeter surfacesfor permitted installations under the 2008 NEC.
http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=70
The premise of the proposal is that self-contained spas and hot tubs should be exempt for the perimeter bonding requirements much like storable pools and indoor spas as permitted in 680.30 and 680.43 - Exception 2, respectfully, of the 2011 NEC.
This has certainly been a hotly debated issue since the inception of the permiter surface bonding concept back in the 2005 NEC. While many code professionals and users have come to grips with all the requirements of 680.26, it has always been a gray area as to how the perimeter surface bonding is to be accomplished for a self-contained spa installed on an existing slab.
While the acceptance of this TIA would only change the 2011 NEC, it may be used as substaniation to not require the bonding of the perimeter surfacesfor permitted installations under the 2008 NEC.
http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=70