In reviewing some drawings with contractor, I have something thats troubling me that I can't put my finger on. The building is designed with (2) 480Y/277 transformers/service centers.
Both services exceed 1200 amp and will have G-F mains. The plans show a "tie breaker" connecting the two systems. Under normal operation, the second service disconnect is open and everything is fed from the 1st service thru the tie-breaker.
In that the second service has the neutral bonded, will this not cause a problem with the G-F device on the 1st service and are we not violtaing 250-24(a).5?