32 units roughed with MC supported by tie wire to the metal studs and the inspector says "no tie wire, must use CJ's". Is tie wire an approved method of supporting MC cable to metal studs?
PrimaryElectric said:32 units roughed with MC supported by tie wire to the metal studs and the inspector says "no tie wire, must use CJ's". Is tie wire an approved method of supporting MC cable to metal studs?
Approved. Acceptable to the authority having jurisdiction.
(C) Supporting. Unless otherwise provided, cables shall
be supported at intervals not exceeding 1.8-m (6-ft)
Horizontal runs of Type MC cable installed in wooden
or metal framing members or similar supporting means
shall be considered supported and secured where such support
does not exceed 1.8-m (6-ft) intervals.
Unfortunately, your AHJ or inspector gets to approve or dissaprove tie wire.PrimaryElectric said:32 units roughed with MC supported by tie wire to the metal studs and the inspector says "no tie wire, must use CJ's". Is tie wire an approved method of supporting MC cable to metal studs?
Tie wire is not specifically stated.330.30 Securing and Supporting.
(A) General. Type MC cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings or other approved means designed and installed so as not to damage the cable.
The inspector does not get to make that choice. Only the AHJ can do that and the inspector is NOT the AHJ.roger said:Unfortunately, your AHJ or inspector gets to approve or dissaprove tie wire.
PrimaryElectric said:32 units roughed with MC supported by tie wire to the metal studs and the inspector says "no tie wire, must use CJ's". Is tie wire an approved method of supporting MC cable to metal studs?
Bob, it depends on where you are, in some locals the inspector can in fact be the AHJ or vice versa.petersonra said:The inspector does not get to make that choice. Only the AHJ can do that and the inspector is NOT the AHJ.
RogerAuthority Having Jurisdiction (AHJ). An organization, office, or individual responsible for enforcing the requirements of a code or standard, or for approving equipment, materials, an installation, or a procedure.
That is not the norm though, although they are often treated that way.roger said:Bob, it depends on where you are, in some locals the inspector can in fact be the AHJ or vice versa.
Roger
petersonra said:That is not the norm though, although they are often treated that way.
The inspector probably has you. I know this won't make you feel any better but, we are allowed to use tie wire here.PrimaryElectric said:The tie wire is used for vertical runs. It is the city of Hollywood, FL.
crossman said:I agree also. Not being able to use tie wire for this application is ridiculous
PrimaryElectric said:32 units roughed with MC supported by tie wire to the metal studs and the inspector says "no tie wire, must use CJ's". Is tie wire an approved method of supporting MC cable to metal studs?
I guess when you fish it in it has a less chance to get "pinched"augie47 said:this logic probably won't help since it may be a case of "my mind is made up, don't confuse me with facts" but since 330.30(D) allows it to be unsupported when fished, next month, after the rock is on, you could fish it thorough the same cavity without support. Kinda makes the type of support used now seem a little insignificant.