Tilt up warehouse bonding

Status
Not open for further replies.
Location
Vancouver
Occupation
Electrical contractor
Currently estimating a tilt up, spec shows bonding required on the perimeter of the footing for the rebar using #3/0 Cu which I have allowed for. Does anyone have experience with the rebar cross pieces in the middle of the slab and if they require bonding as well? I don't think they would as they all have contact to the outside pieces. Don't want to miss something on my estimate
Thanks
 
Welcome to the forum. Can't speak directly to the Canadian code but as far as the NEC the only requirement is a bare #4 to the footing rebar if the steel and concrete qualify. The 3/0 bond sounds like a job spec and any further bonding requirements would likely be found there.
 