Although the owner is going to use lights with sensor in the offices, he does not want to use the sensor for the dog shelter area in his new facility of about 1200 Sq Ft. According to him, since the dogs will be running around in the main room, the sensor will not work. Any idea how to resolve this in Title 24 will be highly appreciated. Thanks a LOT, Samar
either occupancy sensors, or a timeclock are necessary.
occ sensors won't work, so that leaves a timeclock.
you could use a manual on occ switch, but once turned on,
it would never turn off. auto on is a complete nonstarter.
unless you used a wall mounted sensor that wouldn't
trigger with animal sized critters moving around. that's
pretty iffy. dual technology will use the infrared signature
to keep the lights on. nLight uses sound to maintain the
lights on. not gonna work well in a kennel.
for a small occupancy, a straight 2 channel 365 day timeclock
T 20 listed, with a 2 hour wind up bypass timer is probably
your most economical solution. intermatic is my first choice,
as they are easy to program, and bulletproof. use one channel
for interior lighting, with a contactor for multiple circuits, and
the other one for exterior signage. you could also use an nLight
system with a gateway, and make the animal area timed, and
the office area occupancy.
exterior lighting on the structure also need motion sensors.
as animal facilities are often standalone structures, that may
be a consideration.
i do T24 lighting certifications. send me a PM if you want
to discuss making this thing compliant before you install
everything. of late, i'm running into a lot of designs that
are drawn in a way that can't easily be made to comply.
in the last week, i've had three jobs not certify, as they
were drawn noncompliant, and installed as drawn.