Welcome to the Forum. What type of plug? What type of wiring method? i.e. MC ect.tld38 said:I noticed that the 2X4 fixtures we are installing have a plug disconnect at the fixture.
tld38 said:I noticed that the 2X4 fixtures we are installing have a plug disconnect at the fixture. So that if you are daisy chaining you can isolate that fixture without affecting others. Is this a requirement as of 2008 NEC? Thanks much!tld38
Wiring method is mc cable. I should have been more specific, It is a quick disconnect fitting inside the access plate in every fixture, an actual stablock device that you connect your hot & neutral too.chris kennedy said:Welcome to the Forum. What type of plug? What type of wiring method? i.e. MC ect.
480sparky said:It's a quick-connect to mate to the building's wiring system. Unfortunately, you probably didn't wire for it, so you got the wrong fixtures.
It is a quick disconnect fitting inside the access plate in every fixture, an actual stablock device that you connect your hot & neutral too.
tld38 said:Wiring method is mc cable. I should have been more specific, It is a quick disconnect fitting inside the access plate in every fixture, an actual stablock device that you connect your hot & neutral too.
iwire said:No, I don't get that at all, it's just the newly required ballast disconnect
480sparky said:I misread it. You're correct. I was thinking the quick connect was on the MC.