to bond or not to bond?

Status
Not open for further replies.

lotto

Member
Location
ca
I was told to remove my bond from gas to to cold water by one inspector... But the previous inspector insisted that I bond the two in order to receive a final?
 
Technically, wouldn't that be improper gas line bonding if the cold water connection is greater than 5' from building entry and water line is a grounding electrode?
 
I was told to remove my bond from gas to to cold water by one inspector... But the previous inspector insisted that I bond the two in order to receive a final?

How can you "overbond" anything and what in the NEC would prohibit this?
 
I was told to remove my bond from gas to to cold water by one inspector... But the previous inspector insisted that I bond the two in order to receive a final?

Was your gas bond in series or bonding point before the meter possibly making it an electrode? ---- Do you have CSST gas piping run in the building as a branch feed to an appliance? -- under normal circumstances with no CSST run as described you are properly bonded thru a gas appliance branch circuit EGC.

you should ask for code sections from the inspector and give more details for a proper response.
 