I have a question and need some advice.
1) There are two wires from the meter. One hot one neutral. Service does not supply a ground.
2) There is no isolater or service disconnect. The wires from the meter go directly into a square d main distribution panel and directly into a main circuit breaker which supplies other mini circuit breakers via the distribution panel.
3) The grounding rod is connected to the earth bus.
4) I am certain the transformer's neutral is grounded.
The question is should I bond the neutral to the ground or isolate them.
Currently the neutral wire goes into the earth/ground bus bar and then into the main circuit breaker so the neutral is grounded before the main disconnect. The ground from outlets are also conected to the earth/ground bus. So in essence the 3rd socket or ground socket is connected to neutral. Is this a parallel neutral circuit?
Should I isolate the earth and neutral or is ok as it is. I have consulted many and its 50-50. Some say it a boo boo and I should revert back to a TT system while some say its safest.
I don't know if this is a PME system or not? I don't have a main service disconnect other than this main panel.
1) There are two wires from the meter. One hot one neutral. Service does not supply a ground.
2) There is no isolater or service disconnect. The wires from the meter go directly into a square d main distribution panel and directly into a main circuit breaker which supplies other mini circuit breakers via the distribution panel.
3) The grounding rod is connected to the earth bus.
4) I am certain the transformer's neutral is grounded.
The question is should I bond the neutral to the ground or isolate them.
Currently the neutral wire goes into the earth/ground bus bar and then into the main circuit breaker so the neutral is grounded before the main disconnect. The ground from outlets are also conected to the earth/ground bus. So in essence the 3rd socket or ground socket is connected to neutral. Is this a parallel neutral circuit?
Should I isolate the earth and neutral or is ok as it is. I have consulted many and its 50-50. Some say it a boo boo and I should revert back to a TT system while some say its safest.
I don't know if this is a PME system or not? I don't have a main service disconnect other than this main panel.