This issue keeps coming up in my head and to be honest I can not settle on one side of the fence.
When implementing LSI (Long time, Short time, Instananeous) LVPCB (Low Voltage Power Circuit Breakers) for MCC main breakers, do you utilize the instantaneous function or not?
MCCs are only rated for their Short Circuit Withstand rating for 3 cycles. A short downstream of any of the MCC feeds will be cleared by the MCCBs or MCPs. So, the only issue would be when the fault occurs on the buswork of the MCC.
The argument from a Power Systems Engineer that we regularly hire for our Power Systems studies contends that if there is a fault on the buswork, the gear is toast anyway. So, don't utilize the instantaneous function to maintain coordination. This contradicts the settings he utilized for a Arc Flash reduction project that was undertaken before I started working here where the instantaneous functions are being used.
A short circuit downstream may cause an entire MCC and resulting unit outage if the instantaneous function is used which, is much more likely to occur than a fault on the MCC buswork.
However, I am not so sure that a fault on the MCC buswork would cause significant damage if it is cleared instantaneously. This would allow the equipment to be opened up and the situation potentially fixed. It could be a while for a replacement MCC to be installed, potentially keeping the unit down if there are no steam backups for that unit.
My question to all of you is, what do you do for the MCCs at your facilities that incorporate LVPCBs as MCC main breakers? Or, what do you typically default to if the customer does not specify to which they prefer? Basically, which side of the fence does everyone tend to fall on?
When implementing LSI (Long time, Short time, Instananeous) LVPCB (Low Voltage Power Circuit Breakers) for MCC main breakers, do you utilize the instantaneous function or not?
MCCs are only rated for their Short Circuit Withstand rating for 3 cycles. A short downstream of any of the MCC feeds will be cleared by the MCCBs or MCPs. So, the only issue would be when the fault occurs on the buswork of the MCC.
The argument from a Power Systems Engineer that we regularly hire for our Power Systems studies contends that if there is a fault on the buswork, the gear is toast anyway. So, don't utilize the instantaneous function to maintain coordination. This contradicts the settings he utilized for a Arc Flash reduction project that was undertaken before I started working here where the instantaneous functions are being used.
A short circuit downstream may cause an entire MCC and resulting unit outage if the instantaneous function is used which, is much more likely to occur than a fault on the MCC buswork.
However, I am not so sure that a fault on the MCC buswork would cause significant damage if it is cleared instantaneously. This would allow the equipment to be opened up and the situation potentially fixed. It could be a while for a replacement MCC to be installed, potentially keeping the unit down if there are no steam backups for that unit.
My question to all of you is, what do you do for the MCCs at your facilities that incorporate LVPCBs as MCC main breakers? Or, what do you typically default to if the customer does not specify to which they prefer? Basically, which side of the fence does everyone tend to fall on?