mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
I am just curious about something. It seems you have 4 possible generators that can power the loads labeled as ACS. Are they so critical that they need that level of redundancy? That's three transfer switches that have to work correctly to power those loads.
Do you want N+N or N+1 (or +2) redundancy? My first take is to parallel all the large gens- gives more operational and maintenance flexibility. Also makes it easier to add capacity down the line. Downside is the paralleling gear can become the single-point-of-failure (SPOF).
For reliability, with proper maintenance.... and using gensets built for 24/7 operation instead of standby, you should be OK. I'm sure the manufacturers would love to talk with you about that.
I haven't dealt with 900RPM units, but it's common as size goes up, RPM goes down; and in theory they're quieter, not sure I buy that, but the sound is different. My gut says they'd be more reliable, too. You will want continuous-duty if they're going to run that way.
What the total load? Looks like maybe few hundred KVA, so in the grand scheme, not that big. While it's a much larger setup, you might look into how some off-grid ski resorts do it (they're paralleling MW+ sets, though).
Not sure how required backups (life safety/etc) play into this.