Mike McCallister
Trying to determine required ampacity for 3 phase, 240 volt service
70% of loads are 1 phase 240 volt A/C equip. remainder is 110 volt recepts and lights.
Plan to use a 3 phase load center to feed all 240 volt A/C equip. and a 1 phase load center for all 120 volt circuits.
Feed load centers from MDP with 1-3 pole breaker for A/C panel and 1- 2 pole breaker for lighting and recept. loads
I thought I could calculate load for 3 phase A/C panel as follows
KVA 68,000
.............. = amps or ................. = 163.58 amps
240 volts X 1.732 415.68
engineer insist that all loads on 3 phase delta connected sevice must be calculated as if it was 1 phase, since it is an unbalanced system.
KVA 68,000
....... = amps or .................. = 282.33 amps
240 volts 240
KVA 68,000
KVA 68,000
240 volts 240