2005 NEC:
Here's the question: In a Class I, Division 2, Group B, C and D environment utilizing "Z" purge... which of these statements is true?
("Z" purge reduces the inside of the enclosure to unclassified)
Article 501.15(A)(2): In each conduit entry into a pressurized enclosure where the conduit is not pressurized as part of the protection system. Conduit seals shall be installed within 450mm (18") from the pressurized enclosure.
Article 501.15(B)(2)Exc.3: Conduit systems passing from an enclosure or room that is unclassified as a result of pressurization into a Class I, Division 2 location shall not require a seal at the boundary.
I really could use a "definitive" answer on this one.
Thanks,
Here's the question: In a Class I, Division 2, Group B, C and D environment utilizing "Z" purge... which of these statements is true?
("Z" purge reduces the inside of the enclosure to unclassified)
Article 501.15(A)(2): In each conduit entry into a pressurized enclosure where the conduit is not pressurized as part of the protection system. Conduit seals shall be installed within 450mm (18") from the pressurized enclosure.
Article 501.15(B)(2)Exc.3: Conduit systems passing from an enclosure or room that is unclassified as a result of pressurization into a Class I, Division 2 location shall not require a seal at the boundary.
I really could use a "definitive" answer on this one.
Thanks,