To Tin or not to Tin

Status
Not open for further replies.

beanland

Senior Member
Location
Vancouver, WA
For bare copper wire buried in the ground for grounding purposes, is there a justification for tinning the wire? All of the projects I have seen use bare un-tinned copper wire. I have read that where there is salt water, then tinning is needed. What is typical and the preferred? My quick check on wire price is that tinning can add 50% to the cost of the bare wire. Thank you.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
When we did the ground (not just grounding) work for a cellular site, tinned, solid #2 copper was specified.
 