MV metalclad switchgear with 125Vdc control power. Already monitoring the control power, and trip coil. If control power is lost; do I trip the breaker, or just alarm (DCS and local) and leave the breaker in it's current position?
I know distribution circuits typically just alarm cause the utility doesn't want customers in the dark, and Data centers, well, they don't want to trip for any reason, but this is not a sensitive process, or a facility that would be considered critical infrastructure.
My first impression would be to trip on loss, but what, if any is typical?
Cheers~