Ignore that I installed an Eaton CH AFCI/GFCI breaker in my home panel. Pigtailed version.

I did not realize until today that the buss bars are shifted 5/8" to the left. Makes putting the neutral on the new breaker impossible after installation, let alone torquing. Panel is 17 year old main lug.

Has that changed with the advent of PONs?
 
Ignore that I installed an Eaton CH AFCI/GFCI breaker in my home panel. Pigtailed version.

I did not realize until today that the buss bars are shifted 5/8" to the left. Makes putting the neutral on the new breaker impossible after installation, let alone torquing. Panel is 17 year old main lug.

Has that changed with the advent of PONs?
Nope you pop off the screw and then the PON fits but I hate it. Same nuetral bus spacing. Still have long body afci and gfi still too.
 