I don’t understand todays graphic of the day. Apparently a panel board (interior board “guts” of such as a service enclosure) if fed from a transformer must be protected by an overcurrent device on the secondary of a transformer.
However this has not been the case since utility transformers and wiring ARE NOT protected on the system secondary windings of their transformers. Instead an EGC system for equipment is made up to creat a return path for ground fault current with a current draw large enough to effect PRIMARY system and trip the primary side fuse or breaker, cutout.
In todays graphic question it is stated otherwise that the secondary of a transformer must be protected by an overcurrent device.
The only overcurrent device is the main disconnect breaker and branch circuit breakers but the main breaker is on the load side of the feeder? Unless this is what is meant?
Also code does allow both primary and secondary protection to my knowledge
However this has not been the case since utility transformers and wiring ARE NOT protected on the system secondary windings of their transformers. Instead an EGC system for equipment is made up to creat a return path for ground fault current with a current draw large enough to effect PRIMARY system and trip the primary side fuse or breaker, cutout.
In todays graphic question it is stated otherwise that the secondary of a transformer must be protected by an overcurrent device.
The only overcurrent device is the main disconnect breaker and branch circuit breakers but the main breaker is on the load side of the feeder? Unless this is what is meant?
Also code does allow both primary and secondary protection to my knowledge